Alarms > Alarms Overview > Alarm Types and Properties > Analog Points

Analog Points

Analog points have six alarm types. The Low Out-of-Range alarm has the highest precedence. The alarms are listed in the table below in order of precedence. See the PNT Editor - Analog Page for configuration information.

Alarm Alarm Calculation Type Calc Value 1 Calc Value 2 Alarm Color Configurable Bit

Out-of-Range

Value Range

High OOR Value

Low OOR Value

Magenta alarm

Magenta

01

High Deviation

Deviation Value

Deviation Value

N/A

Red alarm

Red

06

High Alarm

Maximum Value

Setpoint Value

N/A

Red alarm

Red

05

High Warning

Maximum Value

Setpoint Value

N/A

Red alarm

Red

04

Low Warning

Minimum Value

Setpoint Value

N/A

Yellow alarm

Yellow

03

Low Alarm

Minimum Value

Setpoint Value

N/A

Yellow alarm

Yellow

02

The High Deviation alarm applies when the value deviates from the previous value by the alarm setpoint. The deviation can be either positive or negative.

Alarm Deadband

Analog points have an Alarm Deadband option. This option applies to alarm resets. The point’s value must clear the deadband value before the alarm bit will be cleared.

Example

If the High Alarm setpoint is 300 and the Alarm Deadband is 10, the value must clear 290 before the alarm bit is reset. The AlarmDeadband option helps prevent chattering.