Analog points have six alarm types. The Low Out-of-Range alarm has the highest precedence. The alarms are listed in the table below in order of precedence. See the PNT Editor - Analog Page for configuration information.
| Alarm | Alarm Calculation Type | Calc Value 1 | Calc Value 2 | Alarm Color | Configurable Bit | |
|---|---|---|---|---|---|---|
|
Out-of-Range |
High OOR Value |
Low OOR Value |
|
Magenta |
01 |
|
|
High Deviation |
Deviation Value |
N/A |
|
Red |
06 |
|
|
High Alarm |
Setpoint Value |
N/A |
|
Red |
05 |
|
|
High Warning |
Setpoint Value |
N/A |
|
Red |
04 |
|
|
Low Warning |
Setpoint Value |
N/A |
|
Yellow |
03 |
|
|
Low Alarm |
Setpoint Value |
N/A |
|
Yellow |
02 |
|
The High Deviation alarm applies when the value deviates from the previous value by the alarm setpoint. The deviation can be either positive or negative.
Analog points have an Alarm Deadband option. This option applies to alarm resets. The point’s value must clear the deadband value before the alarm bit will be cleared.
Example
If the High Alarm setpoint is 300 and the Alarm Deadband is 10, the value must clear 290 before the alarm bit is reset. The AlarmDeadband option helps prevent chattering.